The MVR-T216 transformer protection offers easy-to-use differential protection
together with overcurrent protection for both high and low voltage side of the
transformer.
The MVR-T216 transformer protection relay provides overcurrent protection for
both low voltage and high voltage side of the transformer. In addition to that it
offers earth fault protection, negative sequence overcurrent protection as well
as two independent instances of restricted earth fault protection for utmost
protection of the transformer.

10x Current input (configurable 0.2…10A)
3x Digital input
5x Output relay (4NO, 1CO)
1x IRF output (1CO)
2 x Remote com port (1 x RJ45 Ethernet and 1 x RS-485)
- IEC 61850 Ed1. Modbus TCP/RTU, IEC 60870-5-104/103/101. DNP 3.0. SPA protocols
- DT, IEC or ANSI time/overcurrent curves with settable release delays
- 2 extension slots for additional hardware options
- Event recorder (up to 15 000 events)
- Disturbance recorder (up to 100 disturbance records)
- 2nd and 5th harmonic blocking.
- Automatic verification for the connection group and nominal value settings.
- Overloading and through fault statistics for preventive maintenance.
Available Extension Cards:
- 8x digital inputs (programmable threshold voltage)
- 5x output relays
- Arc-Flash Protection - 4x sensor channels, 2x HSO1. 1x BI *)
- 8x RTD input
- 2x RJ45 100Mb Ethernet & IRIG-B *)
- 2x ST 100Mb Ethernet & IRIG-B *)
- 4x mA outputs - 1 x mA input
- 2x LC 100MB Ethernet (HSR, PRP redundant protocols)
- 2x RJ45 100MB Ethernet (HSR, PRP redundant protocols) *)
- RS-232 - Serial Fiber
Features
Protection Functions:
• (Sensitive) Earth fault protection stages INST, DT or IDMT (ANSI 50N/51N(S))
• Breaker failure protection (ANSI 50BF)
• Cable-end differential protection (ANSI 87)
• Current transformer supervision (ANSI 60L)
• Current unbalance/broken conductor protection stages INST, DT or IDMT (ANSI 46 /R/L)
• Harmonic over-current protection/inrush blocking stages INST, DT or IDMT (ANSI 50H/51H/68)
• Programmable stage (ANSI 99)
• Restricted low-impedance earth fault protection (ANSI 87N)
• Switch onto fault logic (SOTF)
• Three-phase over-current protection INST, DT or IDMT (ANSI 50/51)
• Transformer thermal overload protection (ANSI 49T)
• Transformer, motor or generator differential protection, 2 winding (ANSI 87T/G/M)